Is full load over the opening releived by a masonry arch?
Thank you!
Last edited on Fri Oct 3rd, 2008 04:13 pm by alinaski
|
alinaski Member
| Joined: | Sat Sep 17th, 2005 |
| Location: | NYC, New York USA |
| Posts: | 181 |
| Exams Taken: | GS, LF, ME, BD/MM, CD, SP, BP, BT | | Exams Passed: | GS, LF, ME, BD/MM, CD, SP, BP, BT | | Describes Me: | |
| Status: |
Offline
|
| Mana: |     |
|
Posted: Fri Oct 3rd, 2008 05:04 pm |
|
| Here is image: Attachment: 1633_001.pdf (Downloaded 171 times)
|
InTheDark Member
| Joined: | Fri Mar 23rd, 2007 |
| Location: | |
| Posts: | 44 |
| Exams Taken: | PD, GS, LF, ME, BD/MM, CD, SP, BP, BT | | Exams Passed: | PD, GS, LF, ME, BD/MM, CD, SP, BP, BT | | Describes Me: | |
| Status: |
Offline
|
| Mana: |     |
|
Posted: Fri Oct 3rd, 2008 05:14 pm |
|
There's a steel beam in the section, with an attached iron angle supporting the brick, right?
It's a stiffened jack arch - the brick arch alone is not supporting the full load.Last edited on Fri Oct 3rd, 2008 05:33 pm by InTheDark
|
Gdrinkh2o Member
| Joined: | Tue Sep 25th, 2007 |
| Location: | NY |
| Posts: | 148 |
| Exams Taken: | PD, GS, LF, ME, BD/MM, CD, SP, BP, BT | | Exams Passed: | PD, GS, LF, ME, BD/MM, CD, SP, BP, BT | | Describes Me: | Done! |
| Status: |
Offline
|
| Mana: |     |
|
Posted: Fri Oct 3rd, 2008 06:13 pm |
|
| dont see how the brick could support the load above based on those images. I agree with inthedark, the steel is intended to be the lintel.
|
InTheDark Member
| Joined: | Fri Mar 23rd, 2007 |
| Location: | |
| Posts: | 44 |
| Exams Taken: | PD, GS, LF, ME, BD/MM, CD, SP, BP, BT | | Exams Passed: | PD, GS, LF, ME, BD/MM, CD, SP, BP, BT | | Describes Me: | |
| Status: |
Offline
|
| Mana: |     |
|
Posted: Fri Oct 3rd, 2008 06:24 pm |
|
| Well you can have a jack arch made of masonry units alone (brick or stone) - but the units need to be wedged AND they need to bear on significant masonry masses (AT) either side. Most jack arches in relatively contemporary brick buildings are not truly load bearing.
|
alinaski Member
| Joined: | Sat Sep 17th, 2005 |
| Location: | NYC, New York USA |
| Posts: | 181 |
| Exams Taken: | GS, LF, ME, BD/MM, CD, SP, BP, BT | | Exams Passed: | GS, LF, ME, BD/MM, CD, SP, BP, BT | | Describes Me: | |
| Status: |
Offline
|
| Mana: |     |
|
Posted: Fri Oct 3rd, 2008 06:41 pm |
|
I ask this question because I replace the lintel (angle above the window not I beam).
And lintel (this angle) is not required to be fire protected if :
or full load is relieved by masonry arch (?)
or lintel supports just outer face of masonry - i think it is my case.
|
alinaski Member
| Joined: | Sat Sep 17th, 2005 |
| Location: | NYC, New York USA |
| Posts: | 181 |
| Exams Taken: | GS, LF, ME, BD/MM, CD, SP, BP, BT | | Exams Passed: | GS, LF, ME, BD/MM, CD, SP, BP, BT | | Describes Me: | |
| Status: |
Offline
|
| Mana: |     |
|
Posted: Fri Oct 3rd, 2008 06:41 pm |
|
I ask this question because I replace the lintel (angle above the window not I beam).
And lintel (this angle) is not required to be fire protected if :
or full load is relieved by masonry arch (?)
or lintel supports just outer face of masonry - i think it is my case.
|
alinaski Member
| Joined: | Sat Sep 17th, 2005 |
| Location: | NYC, New York USA |
| Posts: | 181 |
| Exams Taken: | GS, LF, ME, BD/MM, CD, SP, BP, BT | | Exams Passed: | GS, LF, ME, BD/MM, CD, SP, BP, BT | | Describes Me: | |
| Status: |
Offline
|
| Mana: |     |
|
Posted: Fri Oct 3rd, 2008 06:48 pm |
|
| Thank you very much!
|
Gdrinkh2o Member
| Joined: | Tue Sep 25th, 2007 |
| Location: | NY |
| Posts: | 148 |
| Exams Taken: | PD, GS, LF, ME, BD/MM, CD, SP, BP, BT | | Exams Passed: | PD, GS, LF, ME, BD/MM, CD, SP, BP, BT | | Describes Me: | Done! |
| Status: |
Offline
|
| Mana: |     |
|
Posted: Fri Oct 3rd, 2008 08:02 pm |
|
InTheDark wrote: Well you can have a jack arch made of masonry units alone (brick or stone) - but the units need to be wedged AND they need to bear on significant masonry masses (AT) either side. Most jack arches in relatively contemporary brick buildings are not truly load bearing.
I understand how the arch is supposed to work, my comment was in reference to the fact that as drawn there didnt appear to be enough bearing to support any load.
|
Kellhammer Member

| Joined: | Wed Apr 7th, 2004 |
| Location: | Registered Architect, Pennsylvania USA |
| Posts: | 522 |
| Exams Taken: | PD, GS, LF, ME, BD/MM, CD, SP, BP, BT | | Exams Passed: | PD, GS, LF, ME, BD/MM, CD, SP, BP, BT | | Describes Me: | |
| Status: |
Offline
|
| Mana: |     |
|
Posted: Fri Oct 3rd, 2008 08:53 pm |
|
| It looks like the I - beam is supporting the wall above and floor. The outside venneer is being carried on a angle that is down and closer to the outside face. A flat arch could work without the angle. The original design and or as-built construction might have had both in place for some reason that is not apparent the little bit of info you have provided. Or the designer may not had trusted the masonry arch as self- supporting. Could spectulate for days. Bottom line, an independant veneer could be supported by the flat masonry arch.
|
alinaski Member
| Joined: | Sat Sep 17th, 2005 |
| Location: | NYC, New York USA |
| Posts: | 181 |
| Exams Taken: | GS, LF, ME, BD/MM, CD, SP, BP, BT | | Exams Passed: | GS, LF, ME, BD/MM, CD, SP, BP, BT | | Describes Me: | |
| Status: |
Offline
|
| Mana: |     |
|
Posted: Fri Oct 3rd, 2008 10:52 pm |
|
Thank you.
|
King Member

| Joined: | Thu Apr 3rd, 2008 |
| Location: | NYC, New York USA |
| Posts: | 643 |
| Exams Taken: | PD, GS, LF, ME, BD/MM, CD, SP, BP, BT | | Exams Passed: | PD, GS, LF, ME, BD/MM, CD, SP, BP, BT | | Describes Me: | AIA |
| Status: |
Offline
|
| Mana: |     |
|
Posted: Tue Oct 7th, 2008 09:33 pm |
|
Funcationally I don't think this should be considered as Arch even though it is called "Flat Arch".
I think I see a steel angle bolted to the I-beam. The picture is too small to tell.
Attached Image (viewed 166 times):
 Last edited on Tue Oct 7th, 2008 09:42 pm by King
|
Coach Member

| Joined: | Tue Mar 4th, 2008 |
| Location: | USA |
| Posts: | 5076 |
| Exams Taken: | | | Exams Passed: | | | Describes Me: | Architect |
| Status: |
Offline
|
| Mana: |     |
|
Posted: Tue Oct 7th, 2008 09:55 pm |
|
| I agree. That's not an arch, it's a lintel with a brick veneer.
|
Spellcaster Architect

| Joined: | Thu Apr 15th, 2004 |
| Location: | ARCHITECT, LEED AP, USA |
| Posts: | 905 |
| Exams Taken: | PD, GS, LF, ME, BD/MM, CD, SP, BP, BT | | Exams Passed: | PD, GS, LF, ME, BD/MM, CD, SP, BP, BT | | Describes Me: | |
| Status: |
Offline
|
| Mana: |     |
|
Posted: Tue Oct 7th, 2008 09:57 pm |
|
Yes, there is an angle - that's what the original poster said he is concerned with, because he wants to replace it without fire protecting it.
The drawing is a textbook example of a "stiffened jack arch", which isn't really a true arch, that's correct, but nonetheless that's the terminology.
I think the original poster has it correct that since the applicable code is telling him he doesn't need to fire protect that angle if it's only supporting the outer brick wythe he should be ok with replacing it as is.Last edited on Tue Oct 7th, 2008 09:57 pm by Spellcaster
|
alinaski Member
| Joined: | Sat Sep 17th, 2005 |
| Location: | NYC, New York USA |
| Posts: | 181 |
| Exams Taken: | GS, LF, ME, BD/MM, CD, SP, BP, BT | | Exams Passed: | GS, LF, ME, BD/MM, CD, SP, BP, BT | | Describes Me: | |
| Status: |
Offline
|
| Mana: |     |
|
Posted: Fri Oct 10th, 2008 03:13 am |
|
Thank you!
|
second life Member

|
Posted: Sat Oct 18th, 2008 08:51 pm |
|
FYI
This flat arch would need a key stone in the middle if it was to function as a load bearing arch.
|
alinaski Member
| Joined: | Sat Sep 17th, 2005 |
| Location: | NYC, New York USA |
| Posts: | 181 |
| Exams Taken: | GS, LF, ME, BD/MM, CD, SP, BP, BT | | Exams Passed: | GS, LF, ME, BD/MM, CD, SP, BP, BT | | Describes Me: | |
| Status: |
Offline
|
| Mana: |     |
|
Posted: Sun Oct 19th, 2008 03:59 am |
|
Thank you!
|
Unsportsmanlike Conduct Member

| Joined: | Sat Feb 25th, 2006 |
| Location: | A-R-C-H-I-T-E-C-T, Illinois USA |
| Posts: | 577 |
| Exams Taken: | PD, GS, LF, ME, BD/MM, CD, SP, BP, BT | | Exams Passed: | PD, GS, LF, ME, BD/MM, CD, SP, BP, BT | | Describes Me: | |
| Status: |
Offline
|
| Mana: |     |
|
Posted: Mon Oct 20th, 2008 03:43 am |
|
| N/M Last edited on Mon Oct 20th, 2008 03:44 am by Unsportsmanlike Conduct
|
Unsportsmanlike Conduct Member

| Joined: | Sat Feb 25th, 2006 |
| Location: | A-R-C-H-I-T-E-C-T, Illinois USA |
| Posts: | 577 |
| Exams Taken: | PD, GS, LF, ME, BD/MM, CD, SP, BP, BT | | Exams Passed: | PD, GS, LF, ME, BD/MM, CD, SP, BP, BT | | Describes Me: | |
| Status: |
Offline
|
| Mana: |     |
|
Posted: Mon Oct 20th, 2008 03:43 am |
|
alinaski wrote: I ask this question because I replace the lintel (angle above the window not I beam).
And lintel (this angle) is not required to be fire protected if :
or full load is relieved by masonry arch (?)
or lintel supports just outer face of masonry - i think it is my case.
Paint the lintel with intumescent paint and be done with it....
|
alinaski Member
| Joined: | Sat Sep 17th, 2005 |
| Location: | NYC, New York USA |
| Posts: | 181 |
| Exams Taken: | GS, LF, ME, BD/MM, CD, SP, BP, BT | | Exams Passed: | GS, LF, ME, BD/MM, CD, SP, BP, BT | | Describes Me: | |
| Status: |
Offline
|
| Mana: |     |
|
Posted: Mon Oct 20th, 2008 02:16 pm |
|
Yes, You are right. I am trying to do paint in most cases!
|
second life Member

|
Posted: Sat Oct 25th, 2008 06:03 pm |
|
Unsportsmanlike Conduct wrote: alinaski wrote: I ask this question because I replace the lintel (angle above the window not I beam).
And lintel (this angle) is not required to be fire protected if :
or full load is relieved by masonry arch (?)
or lintel supports just outer face of masonry - i think it is my case.
Paint the lintel with intumescent paint and be done with it....
i do lintels like this all the time. i've never done fire protection on any of them, nor have i ever heard anyone requesting it.
|
Unsportsmanlike Conduct Member

| Joined: | Sat Feb 25th, 2006 |
| Location: | A-R-C-H-I-T-E-C-T, Illinois USA |
| Posts: | 577 |
| Exams Taken: | PD, GS, LF, ME, BD/MM, CD, SP, BP, BT | | Exams Passed: | PD, GS, LF, ME, BD/MM, CD, SP, BP, BT | | Describes Me: | |
| Status: |
Offline
|
| Mana: |     |
|
Posted: Sun Oct 26th, 2008 05:15 pm |
|
It depends on the code, Chicago requires steel lintels over 5' to be protected.
|
alinaski Member
| Joined: | Sat Sep 17th, 2005 |
| Location: | NYC, New York USA |
| Posts: | 181 |
| Exams Taken: | GS, LF, ME, BD/MM, CD, SP, BP, BT | | Exams Passed: | GS, LF, ME, BD/MM, CD, SP, BP, BT | | Describes Me: | |
| Status: |
Offline
|
| Mana: |     |
|
Posted: Mon Oct 27th, 2008 02:15 pm |
|
| Thank you!
|