    Default Building Section Vignette: 1st try

    Please review my first attempt at this vignette.
    I worked the vignette as follows:

    1. footings
    2. slab on grade
    3. ext. bearing walls
    4. finished ceiling to establish height
    5. clearance for light fixture & sprinklers
    6. found largest duct size on floor then ducts being cut
    7. joists being cut by section
    8. parapets

    Thanks.
    Attached Files Attached Files
    Last edited by Dezrok; 05-01-2012 at 01:25 AM.

  2. #2
    Join Date
    Feb 2012
    Location
    NJ
    Posts
    40

    Default

    Your slab is not on grade. You are showing it under the grade line.

    The bottom of the footing should be 5' below grade.(Refer to Passing soultion on the Ncarb Guideline)

  3. #3
    Join Date
    Apr 2006
    Location
    San Diego, California, USA
    Posts
    409

    Default

    Good catch! Thanks for pointing that out.

  4. #4
    Join Date
    May 2012
    Posts
    46
    Blog Entries
    1

    Default

    The bottom of footing or top of footing at 5' is acceptable, remember the term below frost line